    Three phase vs single phase

    Good morning - I am not an electrician, but cannot seem to get a consistent answer to my question anywhere else and accordingly would appreciate advice from the knowledgeable members of this forum.

    I have three phase power in my house, but recently installed a inverter for solar power which connects to one of the phases only. For various reasons I would prefer it if I can connect to all three phases, and it seems to me that the easiest (and cheapest) way to do it would be to combine the three phases into a single phase - I really don't have any need for three phase power, electricity load is not significant, have removed under floor heating in most of the rooms when I installed wood floors.
    By asking around I have received the following feedback:
    - Converting to single phase is easy - just join all three power wires into a single input wire (or bridge then 3 inputs on the DB board)
    - a transformer, which is very expensive is required
    - it cannot be done except by the municipality (when I live in a residential estate and is not directly connected to the municipal supply!!). The people who hold this opinion also tells me that I have to replace my meter - the current meter I have merely combines all three phases and is exactly the same meter as my neighbours, who don't have three phase power, have.

    Please guys - what is the correct way of doing this (and for which I can get a CoC) - preferably a method which allows me to reverse the conversion in the unlikely scenario I require three phases in future

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    You can't just bridge the 3 phases of a 3-phase supply together, there will be an almighty bang and best case scenario you'll lose eybrows....worst case is you won't be around to tell the tale.

    To convert to single phase it may be possible to simply remove two of the phases and make them redundant but this will leave you with a relatively small incoming supply which may not be sufficient for your needs. Also any 3-phase appliances you may have would no longer work and the DB may need reconfiguring accordingly. You can still meter the resulting supply using the existing 3-phase meter.

    It may be possible to convert to a larger single phase supply and double-up the conductors in the supply cable and increase the available supply at source but whether or not the existing meter could be used is dependant on the meter itself and its rating.

    A new meter isn't that expensive so I wouldn't let the fact it needs replacing govern your decision about whether to convert. I'd also suggest for a job of this nature you should get a competant electrician in to survey the requirements and give you a quotation.
    _______________________________________________

    _______________________________________________

  3. #3
    New Member
    Join Date
    Jun 2015
    Location
    Pretoria
    Posts
    8
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Thank you Andy - next question, where do I find a competent electrical contractor who can do this for me? Can you recommend someone who can do a proper job which complies with all necessary standards?
    I am in Pretoria and never seem to get hold of the skilled people, long history of problems with service providers.

  4. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    I don't know any contractors in Pretoria I'm afraid but maybe one of the other members here can recommend someone.
    _______________________________________________

    _______________________________________________

  5. #5
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    what rating is your 3 phase supply? look on your main circuit breaker and if you have an accessible council box,look there as well.(on your outside wall)

  6. #6
    New Member
    Join Date
    Jun 2015
    Location
    Pretoria
    Posts
    8
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Good morning Bergie - I really don't know how you guys can survive with the weather in CT, sounds a bit unpleasant
    I attach pics of the meter (residential estate so not a council meter) and the main switches and trip switch on my DB board.Click image for larger version. 

Name:	DB board - main and trip switch.jpg 
Views:	1073 
Size:	57.1 KB 
ID:	5710Click image for larger version. 

Name:	Electricity meter.jpg 
Views:	675 
Size:	77.8 KB 
ID:	5711

  7. #7
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    hi solarfan . your main switch is 50 amps 3 phase. (3 x single pole breakers are used which is not compliant).if you can run your household on 50 amps single phase then you could rewire the db to have everything on 1 phase and not use the other 2. eskom want all the phases to be balanced ,but i wouldnt worry about that. your availability fee every month might be more for 3 phase than single phase.

  8. #8
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Quote Originally Posted by bergie View Post
    your main switch is 50 amps 3 phase. (3 x single pole breakers are used which is not compliant)
    You know what gets me about this sort of thing - how did that ever happen in the first place?

  9. #9
    New Member
    Join Date
    Jun 2015
    Location
    Pretoria
    Posts
    8
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Good morning Dave - if I can hazard a guess. I appointed an architect who was an old school friend of mine to design the house and to supervise the construction - i.e. manage all the sub-contractors etc. and inspect the work to ensure up to standard. A year or two after building the house (and after my old school mate architect suddenly became unavailable) I started finding out that instead of appointing competent sub-contractors he appointed various parties who overcharged me (with his consent and with the full knowledge and consent of the QS) and then gave him and the (QS) a kick-back (while my mate told me that he put the work out to tender and appointed sub-contractors who has an excellent reputation and track record).
    Don't even ask me about the quality of the waterproofing at my house - had to completely redo it about 5 years after the house was built as considerable cost (flat concrete roof and waterproofing under balcony floors - I had to rip up all the tiles and start from scratch), the quality of the paint which was used (lasted all of 3 years), the wood which was used in building all cupboards etc etc.
    End result - I still don't even have a wiring diagram for the house (for some reason it seems that no-one is available all of a sudden), and had to redo a lot of the work performed by the subcontractors. Now you can understand my cynicism when dealing with service providers - I don't really trust too many people anymore (which is why I am on this site asking for referrals to someone in Pta who will do a quality job).
    Lesson learned: Next time - be very aware of what happens during the building phase, get external inspectors to sign-off on all work done, most important don't trust anybody, especially old friends, get everything in writing from everybody

  10. #10
    New Member
    Join Date
    Jun 2015
    Location
    Durban
    Posts
    4
    Thanks
    0
    Thanked 1 Time in 1 Post
    If you discard 2 of the phases you will only have 50 amps available. this may or may not be enough for your house if you have everything on at the same time. you will need to get an Electrician to determine this.

Page 1 of 2 12 LastLast

Similar Threads

  1. Three phase to single phase generator advice needed
    By joshthejew in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 08-Apr-15, 10:12 PM
  2. 320v single phase
    By david2677 in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 03-Jul-14, 09:47 PM
  3. single phase motor advice
    By bergie in forum Electrical Contracting Industry Forum
    Replies: 20
    Last Post: 03-Feb-14, 07:10 AM
  4. [Question] Three phase / Single phase
    By Martinco in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 14-May-12, 10:57 PM
  5. [Question] Single phase and 3 phase testing course
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 3