    New week, but still having the same problem at a house near the sea.
    The E/L always trips when Eskom comes back on after loadshedding. Just to test, i replaced the E/L with a new cbi, split a circuit that was carrying too much load, i have checked all the connections in the DB.

    I try causing a trip by switching off their double pole mains and flick it back up, but it doesnt trip. I dont want to waste the time there so i gave the owner instructions to narrow down where the problem lies by switching off all circuits on earth leakage when power is off, and checking if the E/L has tripped. if not, then we know that the problem is in one of those circuits. (Ive marked the specific cb's to switch off)

    What i wanted to know is are there any other extraneous tests that i have overlooked to help me with this.

    Thanks

  2. #2
    New Member
    Join Date
    Jun 2015
    Location
    Port Shepstone
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Hi Josh, uncanny that! I had exactly the same scenario...changed the ELR etc etc...to no avail initially..although it was an old Elpro one so having changed it seemed to stabilise. It may have something to do with the high in rush current at point of re-energising..but there are more able folk with qualified technical reasons out there im sure!

  3. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,403
    Thanks
    513
    Thanked 854 Times in 687 Posts
    Possibly a voltage spike when the power is restored. If there was a brief spike it would be conducted to earth by surge arrestors in a power supply or an appliance and the RCD could see this as a fault. The earth is functional as well as protective but a 30mA RCD that's supplying the entire installation isn't going to cut much slack if a surge arrestor clamping voltage is exceeded on top of possibly considerable standing background leakage.

    Quote Originally Posted by joshthejew View Post
    ..........I try causing a trip by switching off their double pole mains and flick it back up, but it doesnt trip........
    If you switch L+N together you're more likely to cause an RCD to trip due to N-E capacitive leakage than if you just switch the live.

    **Edit**

    Maybe have a look at this, it might give you some clues;
    _______________________________________________
    I am special and so is Vanash.
    _______________________________________________

  4. #4
    Junior Member
    Join Date
    May 2014
    Location
    Mossel Bay
    Posts
    22
    Thanks
    1
    Thanked 1 Time in 1 Post
    Yea i'm going to have to take a look @ those that might have surge arrestor protection in one of the appliances. the owner runs a home gym, so rowing machines, tredamills are all there. but we never found a fault with them really. But might be the problem. thank you guys very much. will let you know the outcome.

  5. #5
    Junior Member
    Join Date
    May 2014
    Location
    Mossel Bay
    Posts
    22
    Thanks
    1
    Thanked 1 Time in 1 Post
    Oh and thanks Andy for that piece on RCD's. Very useful

Similar Threads

  1. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 23-Jun-15, 11:27 AM
  2. Mains Delay - Life After Loadshedding
    By daveob in forum General Business Forum
    Replies: 13
    Last Post: 19-Jun-15, 09:05 AM
  3. Loadshedding early warning
    By JTech in forum Electrical Load Shedding Forum
    Replies: 9
    Last Post: 22-Apr-08, 03:31 PM
  4. Tripping through the minefield.
    By Dave A in forum BEE and Employment Equity Forum
    Replies: 1
    Last Post: 28-Jul-06, 04:21 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •