    What is the correct procedure to connect a UPS to a load which was originally connected to the main DB.

    Lets take an example, there is a plug circuit in the main DB which runs a server, the client wants a UPS on this line, as he does not want the UPS in the server room.
    The UPS is to be in a separate room as the DB. So effectively the circuit breaker feeding the server, will now be routed to the UPS, and the UPS output line is now fed into the original cable feeding the server room. The UPS has its own circuit breaker in case of an overload or a fault in the line going to the server room.

    My concern here is as follows :-
    1. How does an electrician create the COC for this modification?
    2. There is some maintenance to be done at a later stage on the server room connection, an electrician then switches the circuit breaker for the server room off, however if he is not aware of the UPS, there obviously going to be power on the line at the server room, because the UPS will kick in to maintain power to the server room. What kind of warning material must be placed on the DB board or where ever to ensure that safety is not compromised?
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar and LED lighting solutions - www.microsolve.co.za

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,534
    Thanks
    525
    Thanked 863 Times in 696 Posts
    How big is this UPS? How many KVA? Single or 3 phase?

    If it's a small single phase UPS (<16A input requirement) then just install a 16Amp socket direct from the DB to the UPS location, you can use theMCB that's supplying the existing server cct. Then remove the server room circuit cable from the DB and fit a mountable plug on it after rerouting it to the UPS location. Then install the UPS with a trailing socket on the output side and a trailing plug on the input. Change the label at the DB to indicate the 'UPS Supply' and label the fixed plug as 'Server Room Sockets Supply'. Label every socket in the server room as 'Supplied From UPS'. At this point Bob should hopefully be your uncle.


    Name:  Fixed Plug.jpg
Views: 1338
Size:  2.2 KB
    Mountable Plug (Server room skt cct supplied from this.)

    Name:  Trialing Socket.jpg
Views: 1334
Size:  1.6 KB
    Trailing Socket (Fit to output from UPS)
    _______________________________________________
    I am special and so is Vanash.
    _______________________________________________

  3. Thanks given for this post:

    Justloadit (14-Aug-14)

  4. #3
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    2,703
    Thanks
    89
    Thanked 551 Times in 467 Posts
    Blog Entries
    1
    I think the labeling is the key.
    It is always about safety at the end of the day, over and above the SANAS requirements.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar and LED lighting solutions - www.microsolve.co.za

Similar Threads

  1. Connecting backup generators to existing electrical installation
    By Kevin Stubbs in forum Electrical Load Shedding Forum
    Replies: 35
    Last Post: 20-Jan-16, 07:28 PM
  2. Connecting gas stoves
    By ians in forum Electrical Contracting Industry Forum
    Replies: 23
    Last Post: 15-Jan-15, 05:49 AM
  3. paddle board
    By ians in forum General Chat Forum
    Replies: 2
    Last Post: 31-Jan-14, 06:38 PM
  4. how can I connecting a samsung galaxy s3 to a playstation 3
    By league_of_ordinary_men in forum Technology Forum
    Replies: 2
    Last Post: 29-Oct-12, 06:20 AM
  5. The legal aid board
    By Vanash Naick in forum General Chat Forum
    Replies: 9
    Last Post: 23-Feb-12, 01:18 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •