  1. #1
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts

    3 phase earth leakage protection

    A trick question for all you smart fellas.

    When installing a 3 phase socket outlet in a shop which is only going to feed 1 appliance with a cord not longer than 3 meters, is earth leakage protection required?
    Comments are based on opinion...not always facts....that's why people use an alias.

  2. #2
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    It's certainly possible in terms of 6.7.5.5.

    In fact there's a high possibility for 6.7.5.5 b) to be applicable.

    6.7.5.5 The following do not need earth leakage protection:

    b) a socket outlet that complies with SANS 164-4 and that is intended only for the connection of an appliance for critical application (such as emergency lighting, a deep freeze, a burglar alarm, data processing equipment, or life-supporting equipment);

  3. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    I'd also say it was a possible yes. Lots of variables though, if the socket was fed from a control panel then it could fall outside the general installation regs.
    _______________________________________________

    _______________________________________________

  4. #4
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Will be fed from a standard 3 phase DB. It will be the supply for stationary appliances used for heating and cooking
    Comments are based on opinion...not always facts....that's why people use an alias.

  5. #5
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    i would say it has to be on earth leakage relay. if the socket outlet was dedicated for 1 particular appliance that shouldnt be on earth leakage ,such as alarms,etc then only can it be left off.

  6. #6
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    It all starts at the design of the electrical installations.

    A little while back i got into a dispute with a clever person (electrician) who knew everything and tried to make a fool of me in front of his customer, not a wise move. I may act like a fool most of the time but I do that to protect myself.

    My point is when you design an electrical installations there are a lot of factors which need to be taken into account. One of the reasons i very seldom respond to electrical questions on public forums.

    I have been doing some research into this issue with regards to 3 phase sockets and earth leakage protection and there is some interesting things popping up. For now all i am going to say is not all 3 phase sockets have to be on earth leakage. I need to finish my research before i say anymore.

    The project i am busy with will be hugely affected by earth leakage and i have noted that none of the other installations use earth leakage protection. The meeting with the engineer is going to be rather interesting.

  7. #7
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    I think the simple answer would be that yes, all 3phase sockets would require E/L protection unless they somehow qualify as an exemption. If it's cooking equipment in a commercial kitchen then I'd say it would be a good idea to RCD protect them anyway given the type of abuse they'd usually suffer in that environment. Under normal circumstances I don't see the point of having kitchen equipment on plugs and sockets, it just provides another place where faults can occur.
    _______________________________________________

    _______________________________________________

Similar Threads

  1. Geyser not on earth leakage
    By Goobie in forum Electrical Contracting Industry Forum
    Replies: 21
    Last Post: 03-Jan-19, 05:44 PM
  2. Does a stove need to be on an earth leakage?
    By Leecatt in forum Electrical Contracting Industry Forum
    Replies: 63
    Last Post: 23-Jan-18, 08:26 AM
  3. How to isolate an earth leakage problem
    By ians in forum Electrical Contracting Industry Forum
    Replies: 45
    Last Post: 23-Jun-17, 10:53 AM
  4. Earth Leakage
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-May-13, 12:03 PM
  5. CBI earth leakage units
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 29-Oct-09, 12:44 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •