    Another earthing question

    I went to a photolab yesterday and spoke at great length to the owner. He told me about a problem he's having with one of his R1.2mil procesing machines that is turning into long drawn out saga. The machine is insured and is being repaired by qualified technicians and nobody can fault their service.

    Anyhow, this is what happened; the machine was running and the maid was doing her daily vacuuming rounds. The vacuum cleaner power cord was suffed and the live line touched the metal body of the machine....the machine got fried.

    Ok, so my questions are as follows;
    1. Shouldn't eatch leakage have protected the machine or was the transfer of current so large and fast that bythe time the earth leak breaker responed it was too late.
    2. Why would touching the bodyof the machine fry the electronics, provided of course that the body of the machine has no electrical contact with the machine other than being earthed?
    How easily someone is offended is directly proportional to how stupid they are.
    ~GS Elevator

  2. #2
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    2,671
    Thanks
    88
    Thanked 544 Times in 460 Posts
    Blog Entries
    1
    Theoretically, the ELCB should have tripped, and no further damaged should have been caused.

    However when a running machine is abruptly disconnected from the supply, and if there are huge inductive loads in the running machine, then theoretically an extremely high pulse of power surge is generated at the moment of the power interrupted in the mains supply lines, which could cause some components to fail. Invariably the PSU takes the knock and fails, but the damage may not only be limited to the PSU, under these conditions.

    This the one reason I always recommend a UPS for any electronic controlled system. The UPS gives you time to either correct the mains failure, or to shut the machine down in a controlled manner.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar and LED lighting solutions - www.microsolve.co.za

  3. #3
    Diamond Member adrianh's Avatar
    Join Date
    Mar 2010
    Location
    Cape Town
    Posts
    5,089
    Thanks
    336
    Thanked 808 Times in 642 Posts
    Fair enough but machines are designed to withstand power supply trips. Those machines work all day every day and are bound to have experienced many power supply trips before.
    How easily someone is offended is directly proportional to how stupid they are.
    ~GS Elevator

  4. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,404
    Thanks
    513
    Thanked 855 Times in 688 Posts
    Some machines have a communications system that is earth referenced, a large fault current down the earth could possibly blow coms cards etc. Generally though I wouldn't expect an earth fault to cause damage to the machine and it's impossible to say why it did without a lot more details about the machine itself and what exactly was damaged.
    _______________________________________________
    I am special and so is Vanash.
    _______________________________________________

  5. #5
    Full Member
    Join Date
    Feb 2014
    Location
    Fish Hoek
    Posts
    55
    Thanks
    6
    Thanked 3 Times in 3 Posts
    If the machine was connected to a "clean earth" system and this system is connected back into the general building earthing system and there is an earth/neutral disconnection fault to the ground spike system then theoretically you could have had a return surge through the neutral, hence a fried PSU.

    Then again how many sparkies understand the term "clean earth", there is no way out of this one methinks.
    Apparently there is nothing that cannot happen today.

  6. #6
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    20,981
    Thanks
    3,056
    Thanked 2,463 Times in 2,068 Posts
    Blog Entries
    12
    Quote Originally Posted by Slow Blow View Post
    Then again how many sparkies understand the term "clean earth"
    For those that don't, a little light reading here and here might help.

    The upshot of it all seems to be - have the chassis bonded to the power earth, and the electronics bonded to the clean earth. This way in the o.p situation the energy would all flow through the power earth, (giving your electronics a better fighting chance).
    The trouble with opportunity is it normally comes dressed up as work.

  7. #7
    Platinum Member
    Join Date
    Apr 2010
    Location
    KZN
    Posts
    1,587
    Thanks
    76
    Thanked 138 Times in 118 Posts
    I haven't seen a "clean earth" being used since year dot. even the dedicated plugs no longer have a separate earth. Got involve din some lightning protecting projects at one stage, went to a few seminars and this clean earth separate earth system is not the way to go. What seems to come out was people turning more towards the all in one earth system, where everything is bought to one point and grounded correctly. Just a note I haven't felt the urge to waste my time at seminars etc in while , things might have changed again.

Similar Threads

  1. Vat Question
    By KimH in forum Tax Forum
    Replies: 1
    Last Post: 17-Oct-13, 12:16 PM
  2. November 2010 Paper 2 Exam Question 1 and Question 2 (ANSWERS)
    By Fikani2010 in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 12-May-13, 10:49 PM
  3. Earthing
    By TECHNICIAN 810 in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 23-Feb-12, 10:13 PM
  4. Earthing and the CoC
    By WallyL in forum General Regulatory Compliance Forum
    Replies: 11
    Last Post: 20-Jan-11, 12:06 AM
  5. Question.
    By nilla in forum General Business Forum
    Replies: 3
    Last Post: 26-May-10, 07:08 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •