Thread: How to isolate an earth leakage problem

  1. #21
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Dimming lights is probably caused by voltage dips during peak load times. This is completely different to surges. Surge arrestors won't help protect against voltage dips I'm afraid.

    Most decent electronic items have their own built-in surge protection, if you're living in an area that's notorious for lightning strikes then supplimentary surge protection can't hurt but look at protecting the entire installation by having them installed in your DB rather than just protecting individual appliances with a 'piggy-back' type unit at the plug.
    _______________________________________________

    _______________________________________________

  2. #22
    Email problem
    Join Date
    Apr 2014
    Location
    Somerset West
    Posts
    7
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by ians View Post
    Step 1 : switch off the main switch, earth leakage unit and all the circuit breakers, unplug everything and switch off isolators (stoves, pool, geyser, etc)

    Step 2 : switch on the earth leakage unit first then switch on the main switch, if the earth leakage trips chances are you have a neutral fault, you need to call an electrician. If the earth leakage unit stays up/on go to step 3

    Step 3 : Switch on one circuit breaker at a time and wait a second or 2 as you switch them on, if the earth leakage trips as you switch on a circuit breaker, leave the circuit breaker down/off and move to the next circuit breaker, if the rest of the circuit breakers are reset without tripping the earth leakage unit then you have identified the circuit then you can start plugging appliance back in and switching on isolators, you will find some appliance don't work, you will need to get an electrician to trace the fault. If all the circuit breakers reset without tripping the earth leakage unit, then go to step 4

    Step 4 : Start plugging in appliances and switch on isolators one at a time until the cable/ appliance trips the earth leakage, unplug the appliance which trips the earth leakage and leave it unplugged, you have identified the problem, you don't need to call an electrician, just replace the appliance, if you switch on the pool isolator and it trips the earth leakage you know it is the pool causing the problem.

    Note!!!!
    This is a very basic explanation of what might be causing the earth leakage unit trip and if in doubt call your local electrician.
    Finding an "electrician" capable of tracing faults could be just as tricky as the fault itself
    I have followed the steps above. First time the EL tripped was when I plugged back in the power to my gate motor/lights
    So the potential culprits seems to be my gate motor and/or two lights at my gate which are switched on/off by a light sensor positioned back at the house and wired into the power cable going to the gate.
    I left that unplugged and when I reset the EL it stayed up first time whereas previously I had to do it a few times.

  3. #23
    Email problem
    Join Date
    Apr 2014
    Location
    Somerset West
    Posts
    7
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by fundi View Post
    I have followed the steps above. First time the EL tripped was when I plugged back in the power to my gate motor/lights
    So the potential culprits seems to be my gate motor and/or two lights at my gate which are switched on/off by a light sensor positioned back at the house and wired into the power cable going to the gate.
    I left that unplugged and when I reset the EL it stayed up first time whereas previously I had to do it a few times.
    sorry forgot to mention the gate plug was the last one to be plugged in as it is in my garage.

  4. #24
    Junior Member
    Join Date
    Mar 2014
    Location
    Welkom
    Posts
    24
    Thanks
    0
    Thanked 2 Times in 2 Posts
    If only the 2 lights at the gate are controlled by the photocell, good. If your gate motor is also controlled by it, that 7aH battery is not going to last long.

  5. #25
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    Why have lights @ the gate controlled by a switch @ the back of the house? Mount the switch by the gate. You can get power from the motor, you also have the option of having the gate switching the lights on when it opens, if you do not require the lights to burn all night. This way you will be aware of your gate opening at night by someone other than yourself.

  6. #26
    Email problem
    Join Date
    Apr 2014
    Location
    Somerset West
    Posts
    7
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by Sparks View Post
    Why have lights @ the gate controlled by a switch @ the back of the house? Mount the switch by the gate. You can get power from the motor, you also have the option of having the gate switching the lights on when it opens, if you do not require the lights to burn all night. This way you will be aware of your gate opening at night by someone other than yourself.
    I said back at the house, not at the back of the house, it's actually positioned at the front of the house, but it's a good idea you have, thank u. I actually would prefer the lights not to be on all night as I have a municipal one right at my entrance.

  7. #27
    New Member
    Join Date
    Aug 2015
    Location
    Port Elizabeth
    Posts
    2
    Thanks
    0
    Thanked 0 Times in 0 Posts
    I've done as prescribed and I have located one circuit to be suspect, problem is, I have no appliance connected to any of the plugs

  8. #28
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    Do you have and extension or multiplug plugged in? Is it a mixed circuit with outside lights on it? Does the circuit go outside? Is there a joint outside? Did you have rain just before it tripped? Was a plug changed recently? These questions will also help identify the fault.

  9. #29
    New Member
    Join Date
    Aug 2015
    Location
    Port Elizabeth
    Posts
    2
    Thanks
    0
    Thanked 0 Times in 0 Posts
    I have disconnected everything and switched the CB off. Weird thing, after I disconnected the feed to the plugs and reconnected, the breaker tripped once and a after I reset the EL it stayed on until now. So it is working but I'm still baffled as to what caused the EL trip in the first place, but thanx for your input.

  10. #30
    Full Member MullerR's Avatar
    Join Date
    Jan 2016
    Location
    Lady Grey
    Posts
    44
    Thanks
    3
    Thanked 6 Times in 5 Posts
    Hi Everyone. Im new to the Forum. I am also an Electrician, not long in the trade, so Im still learning alot from experienced guys. I sit with a very confusing problem regarding an earth leakage device. The earth leakage will trip for no apparent reason anytime of the day and when I switch it back on again, it trips instantly. When I switch off the plugs circuits, it switches on again and then I can Switch on again the plug circuits. The Unit trips when pressing the test button, BUT when I do a test with the ELCB tester, it does not trip. In the kitchen is a ready board, feeding from the main DB with an earth leakage and that one trips when testing with the push button and the ELCB Tester. In the garage is also an Earth Leakage device which operates 100% correct. So I changed the Earth Leakage in the house with the one in the garage, cause I though maybe the one in the house is faulty, but it still does the same, does not want to trip when testing with ELCB tester and the one in the garage still work 100%. What can the cause be that it does not want to trip when testing with ELCB tester, but it trips randomly for no reason?

Page 3 of 5 FirstFirst 12345 LastLast

Similar Threads

  1. Geyser not on earth leakage
    By Goobie in forum Electrical Contracting Industry Forum
    Replies: 21
    Last Post: 03-Jan-19, 05:44 PM
  2. Does a stove need to be on an earth leakage?
    By Leecatt in forum Electrical Contracting Industry Forum
    Replies: 63
    Last Post: 23-Jan-18, 08:26 AM
  3. Earth Leakage
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-May-13, 12:03 PM
  4. Random earth leakage problem
    By BillH in forum Electrical Contracting Industry Forum
    Replies: 39
    Last Post: 23-Jan-12, 09:37 PM
  5. CBI earth leakage units
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 29-Oct-09, 12:44 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •