    I had to replace a faulty earth leakage this morning and realised that neither the stove nor the geyser is on the earth leakage. I fixed it by feeding the geyser's circuit breaker from the EL, but it trips the EL as soon as the CB is turned on.

    It is an old house (from 1962) and the DB was brought up to spec when I purchased it 6 years ago. At that time the house still had its low pressure geyser. This old geyser has been disconnected six months ago and the electrical cabling has been extended by 5m to where a new geyser was installed. The new geyser is also controlled by a geyserwise unit.

    My questions:
    1. I've seen it discussed that it is ok for stoves to not be connected to EL. Is that the same for geysers, or do they have to be protected by EL?
    2. could the geyserwise be the cause of the EL trip?

    As soon as it cools down up there I want to start troubleshooting the problem. Apart from bypassing the geyserwise, what else should I check?

    Any help would be much appreciated.

    Thanks

  2. #2
    New Member Esurgeon's Avatar
    Join Date
    Jan 2013
    Location
    Randburg
    Posts
    1
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Hi,

    Your geyser unit must be protected by E/L. This is for shock prevention as water is a direct conductor for electricity. If the geyser is not connected to the E/L it is illegal and very unsafe for your family.

    The trip problem is caused by a neutral to earth problem and your earth leakage tripping is protecting you from danger

    Yes, they cause for the earth leakage tripping can be they geyser wise system but also check
    1. The supply circuit to the geyser (especially the extension point between the old and new wire)
    2. And check your element and thermostat

    Good luck
    Wouter

  3. #3
    Silver Member
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    298
    Thanks
    3
    Thanked 42 Times in 36 Posts
    it may be unsafe,but its not illegal for the geyser to not be on earth leakage.most likely the element that has an earth fault.

  4. #4
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    263
    Thanks
    13
    Thanked 36 Times in 33 Posts
    Quote Originally Posted by Goobie View Post
    1. I've seen it discussed that it is ok for stoves to not be connected to EL.

    Thanks
    Stoves:
    I beg to differ. The following extract from the SANS 10142-1 2009 contradicts this

    6.16.3.3.1 A stove designed to be a free-standing appliance rated above 16 A shall be connected through

    a) a stove coupler which shall comply with SANS 60309-1/IEC 60309-1 (SABS IEC 60309-1) and of dimensions as given in SANS 337 (a
    maximum of 45 A single-phase and 16 A per phase for three phase)
    NOTE 1 Earth leakage protection is not required for the stove circuit when a stove coupler is used.


    Quote Originally Posted by Goobie View Post
    1. Is that the same for geysers, or do they have to be protected by EL?

    Thanks
    Geysers:
    If a geyser is mounted within Zones 1 or 2 in a bathroom then it too needs to be protected by earth leakage protection as indicated in table 7.1 of SANS 10142-1 2009
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  5. #5
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    21,191
    Thanks
    3,075
    Thanked 2,475 Times in 2,079 Posts
    Blog Entries
    12
    Quote Originally Posted by Esurgeon View Post
    Your geyser unit must be protected by E/L.
    Only when in zone 1 or 2 as covered by Lee.

    Quote Originally Posted by Leecatt View Post
    Geysers:
    If a geyser is mounted within Zones 1 or 2 in a bathroom then it too needs to be protected by earth leakage protection as indicated in table 7.1 of SANS 10142-1 2009
    However I disagree with Lee on his interpretation with this one:

    Quote Originally Posted by Leecatt View Post
    Stoves:
    I beg to differ. The following extract from the SANS 10142-1 2009 contradicts this

    6.16.3.3.1 A stove designed to be a free-standing appliance rated above 16 A shall be connected through

    a) a stove coupler which shall comply with SANS 60309-1/IEC 60309-1 (SABS IEC 60309-1) and of dimensions as given in SANS 337 (a
    maximum of 45 A single-phase and 16 A per phase for three phase)
    NOTE 1 Earth leakage protection is not required for the stove circuit when a stove coupler is used.
    I suggest this last line is only included to prevent confusing stove couplers with other forms of socket outlets that must be on earth leakage unit protection, and not to imply that all other forms of stove connections must be on earth leakage unit protection. If that was the intention, I suggest the framing of the stove section would have been "a stove must be on ELU except where it's connected via a stove coupler".
    The trouble with opportunity is it normally comes dressed up as work.

    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services

  6. Thanks given for this post:

    ACEsterhuizen (27-Jan-16)

  7. #6
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    263
    Thanks
    13
    Thanked 36 Times in 33 Posts
    Quote Originally Posted by Dave A View Post
    Only when in zone 1 or 2 as covered by Lee.



    However I disagree with Lee on his interpretation with this one:


    I suggest this last line is only included to prevent confusing stove couplers with other forms of socket outlets that must be on earth leakage unit protection, and not to imply that all other forms of stove connections must be on earth leakage unit protection. If that was the intention, I suggest the framing of the stove section would have been "a stove must be on ELU except where it's connected via a stove coupler".
    Hi Dave, yes O agree with you. I have read further now and the following passage has clarified it:

    6.16.3.2.3 A cooking appliance circuit may also supply one socket-outlet if
    the rating of the socket-outlet does not exceed 16 A and if the following are
    all contained in one control unit (see also 6.15.4.1): Amdt 5
    a) the socket-outlet;
    b) an earth leakage protection device including overcurrent protection for
    protecting the socket-outlet
    ; and
    c) the switch-disconnector required for the cooking appliance (see
    6.16.1).
    NOTE The socket-outlet has to be protected against earth leakage so, unless the
    protection device (see (b) above) is in the control unit, the entire cooking appliance
    circuit has to be protected against earth leakage.


    Sometimes its about what the SANS doesn't say rather than what it does say.
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  8. Thanks given for this post:

    Dave A (15-Jan-13)

  9. #7
    Junior Member
    Join Date
    Jun 2012
    Location
    Riversdale (Garden Route)
    Posts
    23
    Thanks
    4
    Thanked 2 Times in 1 Post

    Looking for pdf-copy (or a CD) of SANS 10142-1

    Quote Originally Posted by Leecatt View Post
    Stoves:
    I beg to differ. The following extract from the SANS 10142-1 2009 contradicts this
    ... as indicated in table 7.1 of SANS 10142-1 2009
    I was just wondering, as I am still looking for a pdf-copy of SANS 10142-1, does this document really have thousands of pages or hundreds of images???

    What I can find on the Internet ranges from about 350mb to 1.5gb as a download.
    Isn't it possible to convert it in a pdf-file with at most 2 digits of mb?

    I am living on a farm and though I got a theoretical downstream bandwidth of up to 2mb (wireless), I cannot really download files that huge.

    Maybe someone can sell me a second hand CD?

    Thanks for your time.

  10. #8
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,540
    Thanks
    525
    Thanked 863 Times in 696 Posts
    To be honest Tato, the regs is one thing I'd urge you to buy an original copy, that way you'll get the ammendments free when they're released. Although there's several unofficial copies up for grabs there's always the possibility that a version from an unknown source could be inaccurate or tampered with. I doubt you'll find a secondhand CD for sale and if your bandwidth is limited it won't even help if you persuade somebody to Dropbox or torrent a copy for you.
    _______________________________________________
    I am special and so is Vanash.
    _______________________________________________

  11. #9
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    263
    Thanks
    13
    Thanked 36 Times in 33 Posts

    Question Rehashing an oldie

    "Earth leakage protection is not required for the stove circuit when a stove coupler is used.


    I've been giving the above line a little more thought. Look at it from another angle:

    Earth leakage protection is required for the stove circuit when a stove coupler is not used.

    And then:

    6.16.3.2.3 A cooking appliance circuit may also supply one socket-outlet if the rating of the socket-outlet does not exceed 16 A and if the following are
    all contained in one control unit (see also 6.15.4.1): Amdt 5
    a) the socket-outlet;
    b) an earth leakage protection device including overcurrent protection for protecting the socket-outlet; and
    c) the switch-disconnector required for the cooking appliance (see
    6.16.1).
    NOTE The socket-outlet has to be protected against earth leakage so, unless the
    protection device (see (b) above) is in the control unit, the entire cooking appliance
    circuit has to be protected against earth leakage
    .


    I read all of this as follows: The stove has to be covered by earth leakage unless it is connected via a stove connector and furthermore if there is an unprotected socket outlet integrated into the stove circuit then the entire combined circuit must be protected by an earth leakage, stove coupler or not.

    Thoughts on this please guys?
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  12. #10
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    21,191
    Thanks
    3,075
    Thanked 2,475 Times in 2,079 Posts
    Blog Entries
    12
    Quote Originally Posted by Leecatt View Post
    Thoughts on this please guys?
    You're going around in circles, Lee

    You're taking the situation where the stove supply also supplies a socket-outlet, and then trying to extend that to where the stove supply does not also supply a socket-outlet - a situation which is covered prior to the clause you quote above.

    The introduction of an earth leakage protection requirement arises from the presence of the socket-outlet.
    (which I hasten to add is differentiated from a stove coupler).
    The trouble with opportunity is it normally comes dressed up as work.

    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services

Page 1 of 2 12 LastLast

Similar Threads

  1. Does a stove need to be on an earth leakage?
    By Leecatt in forum Electrical Contracting Industry Forum
    Replies: 63
    Last Post: 23-Jan-18, 08:26 AM
  2. Earth leakage trips at night??
    By Jongseun in forum Electrical Contracting Industry Forum
    Replies: 18
    Last Post: 18-Jun-12, 10:47 PM
  3. earth leakage unit failure
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 23-Feb-12, 08:37 PM
  4. Random earth leakage problem
    By BillH in forum Electrical Contracting Industry Forum
    Replies: 39
    Last Post: 23-Jan-12, 09:37 PM
  5. CBI earth leakage units
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 29-Oct-09, 12:44 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •