Thanks Sparks. The problem with that is that there is only one neutral in the cable which has to be isolated so therefore all phases would have to be isolated as well which is in contradiction to the regs as far as ""... in order that maintenance work can be carried out without switching off all the lights"
The only option that I can see is to place a D/P isolator at each branch to a fitting which in this case is not going to happen as there are +- 450 fittings.
I will be phoning the ECA today to see what their interpretation is and will report back with the answer.
Baie welkom hier tussen ons. Alhoewel jy welkom is om nog te leer, sien ons ook uit na jou bydrae. Skop gerus jou skoene uit en maak jou tuis. Voel ook vry om enige vrae in Afrikaans te stel. Terminologie kan soms verwarrend wees as dit nie in jou eie taal is nie.
Loer ook gerus by die ander disipline se blaaie in, daar is ook baie interesanthede.
To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.
Is jy die Houtkop wat ek ook ken ?
Martin Coetzee
Supplier of Stainless Steel Band and Buckle and various fastening systems. Steel, Plastic, Galvanized, PET and Poly woven.
We solve your fastening problems.
www.straptite.com
You may never know what results will come from your actions, but if you do nothing, there will be no results... Rudy Malan † 05/03/2011
I contacted the ECA yesterday and spoke to them regarding my installation and that regulation. Their comment was that the regulation commonly applies to a row of lights where the neutrals are looped in and out of fittings. The purpose of the regulation is to prevent a fitting being removed thereby causing a danger with a broken neutral.
I questioned them regarding my application and they are happy that the three phase circuit is supplied through a T/P C/B without any further need of isolators. Personally I dont see how that is correct according to the wording of the regulation but if they are happy then I will continue as the project was originally planned with just a T/P C/B with warning labels in the junction boxes stating three phase supply.
Just more confirmation that ECA have their own ideas about the regs. It clearly states all the phases including the neutral. Being as you say a factory installation I suggest you bring your 3ph cable down to an accessible level and put a lightswitch panel, with DP switches, there for easy access to do maintenance.
Dave A (21-Oct-12)
Ja jou ou kft
Ek stem saam met jou en dan maak jy sommer extra veiligheid vir die "ek doen dit sommer self" customer. Jy moet vir hulle ook dink