    Distribution board over toilet

    No bath and no shower, but can you have the distribution board over the toilet?

    Click image for larger version. 

Name:	ielect pics 066.jpg 
Views:	388 
Size:	41.5 KB 
ID:	2712

    The db is also about 2.2m away from the hand basin.

    Click image for larger version. 

Name:	ielect pics 067.jpg 
Views:	376 
Size:	43.0 KB 
ID:	2713

  2. #2
    Full Member
    Join Date
    Feb 2011
    Location
    JHB, South Africa
    Posts
    58
    Thanks
    0
    Thanked 2 Times in 2 Posts
    I hope that,s not in a bar, nor at a club where Alch gets more than distribution and control... U never know someone might slip off his balance
    "IF YOU WAIT FOR PERFECT CONDITION, YOU'LL NEVER GET ANYTHING DONE"

  3. #3
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,480
    Thanks
    134
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    I suppose it is a smelly situation.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  4. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    As far as I know it wouldn't breach the regs apart from maybe being easily accessible for emergency supply isolation if the cubicle/bathroom is in use and locked.
    _______________________________________________

    _______________________________________________

  5. #5
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    After some careful thought, we're going to apply

    6.6.1.7 A distribution board shall not be mounted

    c) within a radius of 1m from a water tap or valve (in the same room), unless the enclosure provides a degree of protection of at least IP44.

    The next question, given the design - would it be acceptable to insert a rubber strip to seal the door edge against the cover?

  6. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Hmm, I thought the sink was 2 meters away so you must be referring to the toilet flush...which is plastic. To be honest I suspect the enclosure might be IP 44 as it stands even without a rubber door gasket. All the panels with door gaskets that I have in my stock are IP55 or better, I just checked. From what I can see in the photos I would just take a laissez faire stance on this one and give it the benefit of the doubt.

    Click image for larger version. 

Name:	untitled2.jpg 
Views:	332 
Size:	56.0 KB 
ID:	2725
    _______________________________________________

    _______________________________________________

  7. Thanks given for this post:

    Dave A (25-Jul-12)

  8. #7
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Yep - it's the toilet cistern refill valve I'm concerned about. And I believe requiring IP44 is fair enough to cover water flying around if something went faulty there.

    Quote Originally Posted by AndyD View Post
    To be honest I suspect the enclosure might be IP 44 as it stands even without a rubber door gasket.
    Thanks for that guidance - very helpful.

  9. #8
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    You're welcome Dave. Did the setup in the photos pass muster 'as is' or is it still a contentious issue?
    _______________________________________________

    _______________________________________________

  10. #9
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Nope, the photos did the trick as is and I managed to join the dots.

    For IP44 the circuit breakers must be covered, not open - but the cover doesn't have to be tightly sealed at the joint to the db (which would make it IP55)

  11. Thanks given for this post:

    AndyD (27-Jul-12)

Similar Threads

  1. Durban to host World Toilet Summit
    By Blurock in forum General Chat Forum
    Replies: 12
    Last Post: 20-Mar-12, 07:51 AM
  2. [Article] toilet paper
    By Sarah Wang in forum General Business Forum
    Replies: 0
    Last Post: 13-Oct-11, 03:30 PM
  3. Distribution Board regulations
    By Duncan in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 28-Feb-11, 09:03 AM
  4. Will Toilet Training Work?
    By Debbiedle in forum General Business Forum
    Replies: 7
    Last Post: 21-Feb-07, 07:17 PM
  5. documentation and information distribution
    By duncan drennan in forum General Business Forum
    Replies: 2
    Last Post: 23-Oct-06, 07:53 AM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •