    Problem with outside lights

    Hey guys I was just wondering if you could help me out please,I installed 2 outside lights eurolux FS96 floodlights about 2 months ago and been working fine.Yesterday the power was off most of the day,when they were suppose to come on the lamps started flickering and only 1 came on,tonight there doing the same one flickers and the other one doesn't do a thing.I checked the voltage and it was 183v at the light fitting then I checked the power at the mains and it was 189V,the sockets were 180v.do you think the power could be affecting the lights?

    Scott

  2. #2
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    190 volts is very low. better get eskom in there quick before your appliances fry.

  3. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Wow, 180v at the sockets! I'm surprised anything electronic is working in that house. I would test the lights on a 220v supply before going any further. Why is the voltage so low? Is the neutral voltage elevated? I would run the usual barrage of tests at the incoming supply and see if the problem is in the house or Eskom.
    _______________________________________________

    _______________________________________________

  4. #4
    Full Member
    Join Date
    Feb 2011
    Location
    Scotland
    Posts
    46
    Thanks
    2
    Thanked 5 Times in 4 Posts
    Morning guys,I checked the sockets this morning and the voltage was 197 and the same at the mains.I never done any other tests but I will do when I get home and I will let you guys know.

  5. #5
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,479
    Thanks
    134
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Just a question -
    Is the battery in your meter good?
    is your meter reading correctly?
    How did you test your meter?
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  6. #6
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Power out for most of the day.
    Voltage problems there after.
    Coincidence? Probably not.

  7. #7
    Full Member
    Join Date
    Feb 2011
    Location
    Scotland
    Posts
    46
    Thanks
    2
    Thanked 5 Times in 4 Posts
    The municipality came out this morning and they said the clips on the mains cable in the street weren't on correctly and it was a new cable that was installed a few weeks back.there is now 210v at the mains and the outside lights are working.
    The tester is brand new and so are the batteries

    Scott

  8. #8
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Well 210volts is still a little on the low side but a step in the right direction from being in the 180's range. Might be worth putting the installation under a decent load and rechecking the DB supply voltage and neutral-earth voltage etc. Glad to hear it's all working again anyway.
    _______________________________________________

    _______________________________________________

  9. #9
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    at least its not 380 volts. i have seen a few times where city council gets mixed up and then they have to kak en betaal

  10. #10
    Full Member
    Join Date
    Apr 2012
    Location
    Vaal Triangle
    Posts
    55
    Thanks
    2
    Thanked 5 Times in 5 Posts
    Well, if you train your artisans over a period of 18 months, module based, this is what happens. Problems.

Page 1 of 2 12 LastLast

Similar Threads

  1. Low voltage down lights and ceiling earth bar
    By ColinK in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 08-Jul-11, 03:32 PM
  2. lem lights
    By murdock in forum Energy and Resource Conservation Forum
    Replies: 7
    Last Post: 09-Dec-10, 09:04 AM
  3. [Article] Portable electric lights
    By Master Electrician in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 17-Sep-10, 09:54 PM
  4. Don't forget to switch out the lights.
    By Dave A in forum Business Finance Forum
    Replies: 0
    Last Post: 16-Jan-09, 03:23 PM
  5. And the lights go out again.
    By Dave A in forum Electrical Load Shedding Forum
    Replies: 71
    Last Post: 25-Feb-08, 04:38 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •