Thread: Disconnecting a gate motor

  1. #61
    Full Member
    Join Date
    Jun 2014
    Location
    Somerset West
    Posts
    42
    Thanks
    3
    Thanked 5 Times in 5 Posts
    OK, I have been advised that it must in fact be within 1.5m of the appliance / motor. I do however feel that SANS is not clear enough on their wording.

    6.16.1.5 The disconnecting device shall be positioned:
    a) within 1,5 m from the appliance

  2. #62
    Suspended
    Join Date
    Mar 2013
    Location
    Had enough
    Posts
    3,358
    Thanks
    114
    Thanked 213 Times in 201 Posts
    Yep - so the 1m is correct ...... if it has to be within 1.5 and the "visible" one is very ambiguous.

  3. #63
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    "Arm's length" and "arm's reach" are somewhat different from each other as are: "visible", "in sight" and "line of sight". As the responsible person you are expected to ensure that for the specific environment you have provided the best solution considering the regulations as well as that environment.

  4. Thanks given for this post:

    Dave A (04-Mar-16)

  5. #64
    Full Member
    Join Date
    Jun 2014
    Location
    Somerset West
    Posts
    42
    Thanks
    3
    Thanked 5 Times in 5 Posts
    Quote Originally Posted by Sparks View Post
    As the responsible person you are expected to ensure that for the specific environment you have provided the best solution considering the regulations as well as that environment.
    Sure. The trouble comes in where you are issuing a CoC on an existing installation. "Rather safe than sorry" = unnecessary work and expenses for customers.

  6. #65
    Suspended
    Join Date
    Mar 2013
    Location
    Had enough
    Posts
    3,358
    Thanks
    114
    Thanked 213 Times in 201 Posts
    I think the regulations that were brought in for a simple thing like a motor or an electric fence is a good thing. Too many people doing crap work out there and it was one way to regulate

  7. #66
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    Quote Originally Posted by PaulG View Post
    Sure. The trouble comes in where you are issuing a CoC on an existing installation. "Rather safe than sorry" = unnecessary work and expenses for customers.
    If the client took the "safe" route the day it was installed, he would have used an accredited electrician then it would not be a problem when the time came to get a COC to sell the property. Unfortunately, saving a buck and putting the lives of his family at risk is somewhat of a priority for the majority of homeowners.

  8. #67
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    Quote Originally Posted by HR Solutions View Post
    I think the regulations that were brought in for a simple thing like a motor or an electric fence is a good thing. Too many people doing crap work out there and it was one way to regulate
    It would be a good thing if it were enforced.
    There is no national exam as yet for electrical fencing.
    Installers who could prove that they worked for a company installing fences for 2years can apply for accreditation.
    This means the cheap unskilled labour is also elligible for accreditation to certify!!!

    I have refused to certify an installation because the COC for the electric fence was issued despite the energiser not being installed as per basic installation regulations.
    It was mounted on the outside of the garage( no enclosure) with a piece of ripcord going though the wall and into the DB where it was connected to one of the 20A circuit breakers. The hole through the wall was made with a hammer and chisel. I suspect the same tools were used to make a hole through the back of the DB too!

Page 7 of 7 FirstFirst ... 567

Similar Threads

  1. VAT on motor oil
    By J7J in forum Tax Forum
    Replies: 2
    Last Post: 12-Jan-12, 09:46 PM
  2. Electric Motor or Generator ?
    By daveob in forum Electrical Load Shedding Forum
    Replies: 10
    Last Post: 17-Oct-11, 06:01 PM
  3. disconnecting and reconnecting electricty
    By murdock in forum General Business Forum
    Replies: 18
    Last Post: 04-Mar-11, 03:55 PM
  4. Motor winding insulation
    By mikilianis in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 18-Mar-10, 07:30 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •