    3 Phase motor foward/reverse with cam switch

    Hi All

    I have a machine that uses a 1hp 3 phase motor wired into a 3 position cam switch (forward, off, reverse)
    When i run the machine in forward and then toggle it thru the "off" position into the "reverse" position it carries on running in the forward direction.
    If i let it come to an absolute complete stop before i engage the reverse position then it usually works fine and runs in the opposite direction, but not all the time.
    I have tried swapping the phases around on the supply side but it does the same thing (although reverse now = forward and visa versa)
    I know i have come across this before and cant remember what the remedy is.
    Anyone know the answer?

    Thanks

  2. #2
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,480
    Thanks
    134
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Sounds to me like there is a faulty contact on the reverse position side of the switch, as the motor continues turning on 2 phases. It also means the motor is over rated for the application, as the load seems to have no effect on the motor shaft, or else it would have burnt out by now.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  3. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Sounds very odd, usually 3-phase motors have good starting torque in either direction depending on which way around the supply is connected.

    Is the current draw on all three phases the same when the motor supply is connected?
    _______________________________________________

    _______________________________________________

  4. #4
    Email problem
    Join Date
    Jun 2011
    Location
    cape town
    Posts
    2
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Ya you guys are on the money, in reverse the one phase was drawing considerably less current than the other two. Turned out to be a faulty contact on the reverse side.
    Lekker, thanks for the help!

Similar Threads

  1. firemans switch
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 11-Jul-11, 04:51 PM
  2. 3 Phase or 1 Phase.
    By mikilianis in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 10-Nov-10, 07:40 AM
  3. [Question] Phase rotation and PSC
    By Master Electrician in forum Electrical Contracting Industry Forum
    Replies: 14
    Last Post: 06-Sep-10, 12:25 PM
  4. [Question] Single phase and 3 phase testing course
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 26-Feb-09, 09:14 AM
  5. Zimbabwe seeks to reverse brain drain.
    By Dave A in forum General Business Forum
    Replies: 0
    Last Post: 10-Oct-06, 06:19 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •