Page 1 of 3 123 LastLast
Results 1 to 10 of 22

Thread: network analyzer

  1. #1
    Silver Member
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    298
    Thanks
    3
    Thanked 42 Times in 36 Posts

    network analyzer

    any advice on a network analyzer? i,m thinking of buying one to do energy audits.
    which ones do you guys use and where can i buy it in the cape. i would need one that can download to a p.c.

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,534
    Thanks
    525
    Thanked 863 Times in 696 Posts
    I don't understand the connection between a network analyzer and energy auditing.
    _______________________________________________
    I am special and so is Vanash.
    _______________________________________________

  3. #3
    Silver Member
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    298
    Thanks
    3
    Thanked 42 Times in 36 Posts
    i want to leave it connected for a few days to read the kvar,power factor, and load profile,etc.then work out how to save power

  4. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,534
    Thanks
    525
    Thanked 863 Times in 696 Posts
    We just use a standard class1 meter, ip addressable with data logging facilities. ZAPλ 3AM+ Link. If you're in Cape Town they're available through ACDC or Electromechanica.
    _______________________________________________
    I am special and so is Vanash.
    _______________________________________________

  5. #5
    Silver Member
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    298
    Thanks
    3
    Thanked 42 Times in 36 Posts
    thanks andy,but the i think the zapa,s are'nt portable. i see theres a few portable analysers in the electromechanica catalogue,but a bit pricey.even the 5amp clamps are about R 8500

  6. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,534
    Thanks
    525
    Thanked 863 Times in 696 Posts
    Depends on your definition of portable, they're fairly compact, no bigger than a portable unit and they're easy to install in a metering cabinet or in a decent sized commercial DB. The 'portable' power analysers are horrifyingly expensive to do exactly the same data acquisition, plus they're mostly not ipaddressable so won't give real time remote monitoring, they're going to set you back R35K-60K instead of R6K for the Zap meter. Also if you're going to leave a R50K item lying around days on end at a customers premises you should budget for separate insurance as well.

    For current clamps we just use split CT's (a set of 4 costs approx R4000.00) but you can also use the spring loaded hall effect clamps which are far more expensive. You can also use the flexible Rogowski type clamps, very quick and convenient but they're hellishly priced, you might pick up a set for USD1000.00 if you shop around.
    _______________________________________________
    I am special and so is Vanash.
    _______________________________________________

  7. #7
    Silver Member
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    298
    Thanks
    3
    Thanked 42 Times in 36 Posts
    thats good advice,thanks again. what size split CT,s do you use?

  8. #8
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,534
    Thanks
    525
    Thanked 863 Times in 696 Posts
    I have a range of 5A CT's, sets of 100A, 300A, 500A & 1000A. You could probably get away with just a set of 100A and 500A to start with unless you're dealing with larger factory installations. The problem is that for example you get 300A CT's in 2 different diameters to accommodate 2 different busbar sizes. I just purchased the set with the larger form factor and made up some spacing bushes from casting resin to allow the CT's to fit the smaller busbar sizes also.
    _______________________________________________
    I am special and so is Vanash.
    _______________________________________________

  9. #9
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    i use the 3000 amp flex clamps....they are the best...the fluke 435 comes standard with these clamps and you dont need a seperate power supply and you can setup the fluke what range you want internally...but they dont work on my metrel unit...i had to buy another set of 3000 amp flex clamps which have to be powered by an external source...and they have a 30/300/3000 selector problem is is you use batteries they dont las tlong so you have to connect an external power supply...

    fluke have just ome out with the best flex clamp i have seen to date for...it is small enough to fit into all those tight spaces.

    some free advice becareful of this energy/power quality industry....when i started doing it 6 years a go i thought it would be simple...6 years and R200 000 later i am still trying to understand the solutions...collecting the data using the fluke 435 is now as simple as using my fluke 289 but when you have to present solutions to the problem and energy saving tips etc it becomes a whole different ball game...and if you mess up it cost big time...an example a power factor correction unit installed incorrectly....we are busy with an investigation where a R100 000 PFC unit was installed less than a year later R60 000 worth of the components are no longer working...the agents will not replace the components because the installtion was incorrectly designed...the person who sold and installed the unit has suddenly vanished...

    i am not saying dont go into it just becareful....it has also become like the generator bussiness when there was load shedding every man and his uncle is now an expert in this field...there is good money to be made if you know what you are doing...and the market will grow as the price of electricity climbs.

  10. #10
    Silver Member
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    298
    Thanks
    3
    Thanked 42 Times in 36 Posts
    thanks murdock i will keep that in mind. i will start with the existing customers and see how it goes.

Page 1 of 3 123 LastLast

Similar Threads

  1. [Question] Network Marketing
    By BruceHewitt in forum Marketing Forum
    Replies: 13
    Last Post: 03-May-12, 08:56 PM
  2. [Question] Network Marketing
    By Agelfreedom in forum MLM Industry Forum
    Replies: 6
    Last Post: 28-Oct-08, 07:30 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •